Rule condition shows TRUE in UI but Rule never transitions to SET — survives full restart
N
Build: latest-26221-b25bb3e3, Docker on Synology. Hi, I have a Rule whose Trigger/Constraints reference other Rules via Rule State ... is TRUE. At some point it stops firing. Expanding the rule's condition tree in the UI shows every Trigger and Constraint condition green/TRUE — confirmed live by walking into the room and watching Motion go true in real time. Rule History shows no new SET, just old reset entries. Tried, on the same rule, same evening: recreating the trigger conditions with fresh IDs, recreating the constraint conditions with fresh IDs (flat and wrapped in a new Group — wrapping in a Group produced one SET, but it didn't reproduce on repeat attempts with the same structure), and finally a full container restart with a verified-correct saved rule. Still no SET, even with a fresh live motion event right after the restart. Separately, I found that this rule (and its 10 per-room clones) share identical internal condition/group IDs with each other — leftover from a batch clone done months ago, never regenerated. Not sure if that's related, since fixing the IDs didn't reliably fix the symptom either. Has anyone seen a Rule State condition show TRUE in the UI without the Rule ever producing a SET, surviving a clean restart? Thanks in advance
Multi-System Reactor
DynamicGroupController and attributes
therealdbT
Hey @toggledbits I'm back to trying to optimize a couple of things based on dynamic group. First of all, I think I found a typo in the doc: primary_attribute: "binary_sensor.state" primary_attribute_value: | d = false; each id in members: d = getEntity(id)?.attributes?.power_switch?.state or d, d I think the correct code snippet is d = false, All that said, my use case for dynamic groups is to group 3 different climate devices, so I could easily command them at the same time. Commands are good, but sometimes I want to check if any of the devices are on, and that's easily done with a similar snippet as the one you have in the docs. But this is limited to the primary attribute, while I want to have any of the attributes in the group to be driven by a similar logic (while all are null in the group). ie, access hvac_control.mode and see if any of the unit is set to cool, or heat. Is that possible, without re-defining an expression in each of my rules? Thanks!
Multi-System Reactor
Reactor (Multi-System/Multi-Hub) Announcements
toggledbitsT
Build 21228 has been released. Docker images available from DockerHub as usual, and bare-metal packages here. Home Assistant up to version 2021.8.6 supported; the online version of the manual will now state the current supported versions; Fix an error in OWMWeatherController that could cause it to stop updating; Unify the approach to entity filtering on all hub interface classes (controllers); this works for device entities only; it may be extended to other entities later; Improve error detail in messages for EzloController during auth phase; Add isRuleSet() and isRuleEnabled() functions to expressions extensions; Implement set action for lock and passage capabilities (makes them more easily scriptable in some cases); Fix a place in the UI where 24-hour time was not being displayed.
Multi-System Reactor
Unofficial thread for compatibility
tunnusT
As there are statements about compatibility for home assistant versions in MSR new version announcements (e.g. "HassController: Bless Hass to 2025.7.3"), I thought it would be good idea to track other controllers as well. As an example, I can confirm that build "latest-25208-c53e8513" works with Hubitat Elevation C-8 platform version 2.4.2.134 using Maker API. Updates: (the latest versions first in the list) OK: build "latest-25264-2fbe9217" with Hubitat C-8 platform v. 2.4.3.123
Multi-System Reactor
Ooops - Deleted Reactor Ex Machina II
R
I accidentally deleted Reactor Ex Machina II (REM II) from my Reactor rules. I tried to recover it by deleting the .json and .dval in the Rules subdirectory and then recreating it from Togglebits original posting, but that did not work. Does anyone know how to recover REM ll ?
Multi-System Reactor
Bail out of failed reaction?
T
Topic thumbnail image
Multi-System Reactor
Arming Envisalink panel from MSR
T
Topic thumbnail image
Multi-System Reactor
[Solved] DynamicGroupController updating members issue
CrilleC
Edit: Solved in latest-26221. Bare-metal latest-26193 I have this group: "OKforLarm": name: OK för Larm select: - include_controller: vera - include_capability: door_sensor filter_expression: entity.attributes.door_sensor.state It contains the entities I expect but behaves a bit odd. When I open vera>device_10097 the entity attribute door_sensor.state changes to true but it won't show up as member in the group, when I also open vera>device_10095 they both shows as members and when I close vera>device_10095 it disappear from the group but when I close vera>device_10097 it lingers in the group until I restart Reactor.
Multi-System Reactor
Upgrade Issues
T
Topic thumbnail image
Multi-System Reactor
[SOLVED] Conflicting Set Reaction Groups Appear to Fire Simultaneously in Single Rule Evaluation
G
Topic thumbnail image
Multi-System Reactor
[SOLVED] Question regarding "in" vs "contains" vs contents of the string
G
Topic thumbnail image
Multi-System Reactor
Logon screen timeout
G
Noticing since 170 that the lock screen doesn't switch to the logon prompt but, rather, stays on the active UI until such time as you go to click something within it. Then it jumps to the login screen. Brave browser Brave 1.92.139 (Official Build) (arm64) Chromium: 150.0.7871.114
Multi-System Reactor
[MSR] Copy&past of actions and/or drag&drop between set/reset
therealdbT
Hey @toggledbits One thing that bothers me while doing work on new systems/new features, is that I cannot copy&paste actions, and I cannot drag&drop between set and resets. #1 is for when I want to copy an action between different rules opened in two separate browser windows, while #2 is when I just need to flip a bunch of actions in the reset, or move some logic back and forth. Both will be appreciated, but I understand the technical challenges. Thanks!
Multi-System Reactor
Upgrade advice - upgrade from aarch64 to ARM64 image
T
I'm currently on version 26011. I understand that the aarch64 image is no longer supported. So, I therefore need to update to the ARM64 image. Can anyone possibly suggest how I update my docker compose.yaml file (see below). Ideally I'd like to keep my existing reactions etc. rather than start from scratch. # Multi-System Reactor template docker-compose.yml (version 22160) # # Change the lines indicated by "DO"... # services: reactor: container_name: reactor environment: # DO change the TZ: line to set your local time zone. # See valid TZ list: https://en.wikipedia.org/wiki/List_of_tz_database_time_zones TZ: GB # # DO NOT change this path. Your directory location is in "source" below. REACTOR_DATA_PREFIX: /var/reactor # DO change the image below to the one you are using (e.g. armv7l or aarch64 for RPi 4) image: toggledbits/reactor:latest-aarch64 restart: "always" expose: - 8111 ports: - 8111:8111 volumes: # DO change the /home/username/reactor below to the directory you created for # your local data; DO NOT change the /var/reactor part - /home/pi/docker/reactor:/var/reactor - /etc/localtime:/etc/localtime:ro tmpfs: /tmp
Multi-System Reactor
Alexa for MSR, any interest?
MikeReadingtonM
Topic thumbnail image
Multi-System Reactor
[RESOLVED] Telegram notification broke with latest update
3
Topic thumbnail image
Multi-System Reactor
[RESOLVED] Phantom device, “INFO” appears
wmarcolinW
Topic thumbnail image
Multi-System Reactor
[RESOLVED] Mode Status NULL
wmarcolinW
Topic thumbnail image
Multi-System Reactor
[RESOLVED] HTTP query failing after version 26177
wmarcolinW
Topic thumbnail image
Multi-System Reactor
Question about the find function
wmarcolinW
Topic thumbnail image
Multi-System Reactor

Flapping device

Scheduled Pinned Locked Moved Multi-System Reactor
8 Posts 2 Posters 2.1k Views 2 Watching
  • Oldest to Newest
  • Newest to Oldest
  • Most Votes
Reply
  • Reply as topic
Log in to reply
This topic has been deleted. Only users with topic management privileges can see it.
  • tunnusT Offline
    tunnusT Offline
    tunnus
    wrote on last edited by tunnus
    #1

    Got a warning that "Rule is being throttled because its update rate exceeds 60 updates per minute. Check for logic errors that may be causing an evaluation loop, or devices that are "flapping".

    Device in question here is Aeotec Smart Switch 6 connected to Vera Plus, and its configuration is below:

    Screenshot 2021-08-31 at 13.13.22.png

    Shouldn't be an evaluation loop as the rule is very simple (two AND'ed conditions where the first checks whether alarm state is "disarmed" and the second if smart switch power switch state is false).

    Noticed though at the time of warning that wattage measured/reported was changing quite rapidly, so even though wattage was not used in the rule, could that be the reason for throttling? If so, is there anything else that could be done other than raising minimum change values in device configuration? Would like to retain sensitivity for other purposes.

    Using MSR on Docker (Synology NAS), having InfluxDB, Grafana & Home Assistant, Zigbee2MQTT & ZWA-2

    1 Reply Last reply
    0
    • toggledbitsT Offline
      toggledbitsT Offline
      toggledbits
      wrote on last edited by
      #2

      We'd need to see the rule (and any rules/reactions that affect the device), not just the device, to make a determination about why it's flapping.

      Author of Multi-system Reactor and Reactor, DelayLight, Switchboard, and about a dozen other plugins that run on Vera and openLuup.

      tunnusT 1 Reply Last reply
      0
      • toggledbitsT toggledbits

        We'd need to see the rule (and any rules/reactions that affect the device), not just the device, to make a determination about why it's flapping.

        tunnusT Offline
        tunnusT Offline
        tunnus
        wrote on last edited by
        #3

        @toggledbits here's the rule:

        Screenshot 2021-09-02 at 0.05.53.png

        Using MSR on Docker (Synology NAS), having InfluxDB, Grafana & Home Assistant, Zigbee2MQTT & ZWA-2

        1 Reply Last reply
        0
        • toggledbitsT Offline
          toggledbitsT Offline
          toggledbits
          wrote on last edited by toggledbits
          #4

          Pretty straightforward. I'm guessing it's the percentage change that's the issue. With the threshold set at 10%, a change of just 1W when the total wattage is 10W or less will send an update, for example. Some deeper examination of the range in which the excess reports occur may lead you to better values for the configuration. A device that is generating that much traffic (more than one transaction per second) is probably going to lead to other problems in the mesh on Vera, since neither getting busy nor narrow timing are strong points of the Vera ZWave stack. You may be able to address momentary drops in power demand (such as when the motors pause) by using "delay reset" or "sustained for" options to dampen spikes and drops in the device's behavior. This would also then reduce the demand on the device for high accuracy and frequent updates, and let you configure these values to let it be less chatty. I mean, if you're using this to signal you when the wash is done, do you need to know to the second?

          If you really don't want to reconfigure the device, you can set the update rate higher in the engine section of reactor.yaml by setting update_rate_limit to some value higher than 60 (the default). That's a system-wide setting, so it applies to everything.

          Author of Multi-system Reactor and Reactor, DelayLight, Switchboard, and about a dozen other plugins that run on Vera and openLuup.

          tunnusT 1 Reply Last reply
          1
          • toggledbitsT toggledbits

            Pretty straightforward. I'm guessing it's the percentage change that's the issue. With the threshold set at 10%, a change of just 1W when the total wattage is 10W or less will send an update, for example. Some deeper examination of the range in which the excess reports occur may lead you to better values for the configuration. A device that is generating that much traffic (more than one transaction per second) is probably going to lead to other problems in the mesh on Vera, since neither getting busy nor narrow timing are strong points of the Vera ZWave stack. You may be able to address momentary drops in power demand (such as when the motors pause) by using "delay reset" or "sustained for" options to dampen spikes and drops in the device's behavior. This would also then reduce the demand on the device for high accuracy and frequent updates, and let you configure these values to let it be less chatty. I mean, if you're using this to signal you when the wash is done, do you need to know to the second?

            If you really don't want to reconfigure the device, you can set the update rate higher in the engine section of reactor.yaml by setting update_rate_limit to some value higher than 60 (the default). That's a system-wide setting, so it applies to everything.

            tunnusT Offline
            tunnusT Offline
            tunnus
            wrote on last edited by
            #5

            @toggledbits thanks for the analysis & advice! I'm actually using this rule for a simple task that it enables power back to washing machine when in disarmed state. There's a similar rule to cut the power when in "armed away" state.

            Not relating to MSR, but cannot seem to trigger configuration update for this smart switch:

            Screenshot 2021-09-02 at 11.37.59.png

            Did both "save changes" and "apply changes", but both only trigger luup reload and configuration stays the same...

            Using MSR on Docker (Synology NAS), having InfluxDB, Grafana & Home Assistant, Zigbee2MQTT & ZWA-2

            1 Reply Last reply
            0
            • toggledbitsT Offline
              toggledbitsT Offline
              toggledbits
              wrote on last edited by
              #6

              Hard refresh your browser after reloading Luup. It's a UI bug in UI7.

              Author of Multi-system Reactor and Reactor, DelayLight, Switchboard, and about a dozen other plugins that run on Vera and openLuup.

              tunnusT 2 Replies Last reply
              0
              • toggledbitsT toggledbits

                Hard refresh your browser after reloading Luup. It's a UI bug in UI7.

                tunnusT Offline
                tunnusT Offline
                tunnus
                wrote on last edited by
                #7

                @toggledbits did that, and also "configure node right now", nothing seems to change the actual configuration 😞

                Using MSR on Docker (Synology NAS), having InfluxDB, Grafana & Home Assistant, Zigbee2MQTT & ZWA-2

                1 Reply Last reply
                0
                • toggledbitsT toggledbits

                  Hard refresh your browser after reloading Luup. It's a UI bug in UI7.

                  tunnusT Offline
                  tunnusT Offline
                  tunnus
                  wrote on last edited by
                  #8

                  @toggledbits Coming back to this, eventually I was able to change the configuration (below), but still, whenever the washing machine is running, I keep getting the same alerts.

                  Screenshot 2021-10-14 at 16.00.53.png

                  These two rules that are mentioned in the alerts do not even trigger at the time of alerts, because not all conditions are true (see previous posts, where washing machine power switch state should be false for the rule to be triggered).

                  Using MSR on Docker (Synology NAS), having InfluxDB, Grafana & Home Assistant, Zigbee2MQTT & ZWA-2

                  1 Reply Last reply
                  0
                  • toggledbitsT toggledbits locked this topic on
                  • wmarcolinW wmarcolin referenced this topic on
                  Reply
                  • Reply as topic
                  Log in to reply
                  • Oldest to Newest
                  • Newest to Oldest
                  • Most Votes


                  Recent Topics

                  • Rule condition shows TRUE in UI but Rule never transitions to SET — survives full restart
                    N
                    noelab
                    0
                    8
                    54

                  • DynamicGroupController and attributes
                    toggledbitsT
                    toggledbits
                    1
                    9
                    239

                  • Reactor (Multi-System/Multi-Hub) Announcements
                    toggledbitsT
                    toggledbits
                    5
                    149
                    135.1k

                  • Unofficial thread for compatibility
                    tunnusT
                    tunnus
                    2
                    2
                    710

                  • Ooops - Deleted Reactor Ex Machina II
                    toggledbitsT
                    toggledbits
                    0
                    2
                    61

                  • Bail out of failed reaction?
                    T
                    tamorgen
                    0
                    3
                    102

                  • Arming Envisalink panel from MSR
                    T
                    tamorgen
                    0
                    7
                    324

                  • [Solved] DynamicGroupController updating members issue
                    CrilleC
                    Crille
                    0
                    5
                    241

                  • Upgrade Issues
                    T
                    tbully
                    0
                    9
                    348

                  • [SOLVED] Conflicting Set Reaction Groups Appear to Fire Simultaneously in Single Rule Evaluation
                    toggledbitsT
                    toggledbits
                    0
                    10
                    461

                  • [SOLVED] Question regarding "in" vs "contains" vs contents of the string
                    G
                    gwp1
                    0
                    5
                    229

                  • openLuup console disappeared - 500 - Internal Server Error
                    A
                    a-lurker
                    0
                    2
                    246
                  Powered by NodeBB | Contributors
                  Hosted freely by 10RUPTiV - Solutions Technologiques | Contact us
                  • Login

                  • Don't have an account? Register

                  • Login or register to search.
                  • First post
                    Last post
                  0
                  • Categories
                  • Recent
                  • Tags
                  • Popular
                  • Unsolved