Constraints (no data) rule actions have never run
I have a problem rule it seems. Its set to turn off my Festoon lights at 23:55pm and in the constraints checks if those lights are already turned on ?
And the reaction is to turn them off.
Since I setup the rule my lights have never turned off.
In the summary card I can see (no data)
On this screen shot it says the power switch state is TRUE.
The switch is actually OFF at the moment, I have hard refreshed the browser but it still says True.I can go to Scope and add a trace on this device and it does track if its turned on or off OK.
The device is one side of a Fibaro Dual Relay module.
Any clues?
Changes to devices or other dependencies in the Constraints do not cause evaluation of the rule's conditions (triggers or constraints). Only Triggers do that. You would have to wait until after 23:55, which is the only trigger, for the Constraints to be evaluated.
@toggledbits OK think that makes sense.
Not sure why my rules action is not running then.
This is the trigger
I have pressed the Play button in the Set Reaction area and it does actually turn off the light OK.
I've had this rule setup for maybe 3 days and my Festoon lights have never turned off and have been left on all night.
Have you looked in the log at around the time the rule would be expected to trigger? There may be something logged. Remember to adjust for time zone if your host's configured time zone is different from your browser/desktop (i.e. it's not unusual to have a Pi, for example, default to UTC, so all times logged will be UTC and thus maybe different from your local time).
I have other Schedules in MSR for certain times in the morning to open window coverings they are now all working fine and open on the time I set in their triggers.
If I use the command "date" on the Pi in putty it does say the correct time as of now:
Fri 26 Feb 13:15:22 GMT 2021
I'll have a look in the Reactor logs
Looking in reactor.log I searched this rules ID code kljc5802:
2021-02-25T19:00:05.003Z <Engine:INFO> Engine#1 master timer tick, local time "2/25/2021, 19:00:05" (TZ offset 0 mins from UTC) false false2021-02-25T19:34:00.006Z <Rule:5:Rule.js:635> Rule#rule-kljc5802 launching eval from timer-trigger notification by Timer#cond57lqecd false false2021-02-25T19:34:00.009Z <Rule:5:Rule.js:697> Rule#rule-kljc5802 (Schedule - Festoon Lights OFF) evaluate() acquiring mutex false false2021-02-25T19:34:00.012Z <Rule:5:Rule.js:635> Rule#rule-kljbrk9g launching eval from timer-trigger notification by Timer#cond57lqecd false false2021-02-25T19:34:00.014Z <Rule:5:Rule.js:697> Rule#rule-kljbrk9g (Schedule - Lawn Lights OFF) evaluate() acquiring mutex false false2021-02-25T19:34:00.017Z <Rule:5:Rule.js:700> Rule#rule-kljc5802.evaluate() mutex acquired, evaluating false false2021-02-25T19:34:00.021Z <Rule:5:Rule.js:704> Rule#rule-kljc5802 update rate is 0/min limit 60/min false false2021-02-25T19:34:00.023Z <Rule:5:Rule.js:654> Rule#rule-kljc5802 evaluateExpressions() with 0 expressions false false2021-02-25T19:34:00.025Z <Rule:null> Rule#rule-kljc5802 cond cond57lqecd trange after sdt=2/25/2021, 23:55:00 edt=2/25/2021, 19:34:00 now=2/25/2021, 19:34:00 false false2021-02-25T19:34:00.028Z <Rule:null> Rule#rule-kljc5802 cond cond57lqecd timer now scheduled for 2/25/2021, 23:55:00, 15659 secs from now false false2021-02-25T19:34:00.030Z <Rule:5:Rule.js:714> Rule#rule-kljc5802.evaluate() trigger state false (was false) false false2021-02-25T20:13:27.338Z <Engine:5:Engine.js:550> Engine#1 (re-)starting rule Rule#rule-kljc5802 (Schedule - Festoon Lights OFF) 2021-02-25T20:13:27.340Z <Rule:5:Rule.js:555> Rule#rule-kljc5802 start(), awaiting mutex2021-02-25T20:13:27.513Z <Rule:5:Rule.js:563> Rule#rule-kljc5802 restored states: trig=false, rule=false 2021-02-25T20:13:27.515Z <Rule:5:Rule.js:563> Rule#rule-kljc5802 subscribing to dependencies 2021-02-25T20:13:27.517Z <Rule:INFO> Rule#rule-kljc5802 (Schedule - Festoon Lights OFF) started2021-02-25T20:13:27.761Z <Rule:5:Rule.js:700> Rule#rule-kljc5802.evaluate() mutex acquired, evaluating 2021-02-25T20:13:27.762Z <Rule:5:Rule.js:704> Rule#rule-kljc5802 update rate is 0/min limit 60/min 2021-02-25T20:13:27.765Z <Rule:5:Rule.js:654> Rule#rule-kljc5802 evaluateExpressions() with 0 expressions 2021-02-25T20:13:27.767Z <Rule:null> Rule#rule-kljc5802 cond cond57lqecd trange after sdt=2/25/2021, 23:55:00 edt=2/25/2021, 20:13:00 now=2/25/2021, 20:13:27 2021-02-25T20:13:27.771Z <Rule:null> Rule#rule-kljc5802 cond cond57lqecd timer now scheduled for 2/25/2021, 23:55:00, 13292 secs from now 2021-02-25T20:13:27.774Z <Rule:5:Rule.js:714> Rule#rule-kljc5802.evaluate() trigger state false (was false)2021-02-26T00:00:00.129Z <Rule:5:Rule.js:635> Rule#rule-kljc5802 launching eval from timer-trigger notification by Timer#cond57lqecd 2021-02-26T00:00:00.131Z <Rule:5:Rule.js:697> Rule#rule-kljc5802 (Schedule - Festoon Lights OFF) evaluate() acquiring mutex 2021-02-26T00:00:00.136Z <Rule:5:Rule.js:635> Rule#rule-kljbrk9g launching eval from timer-trigger notification by Timer#cond57lqecd 2021-02-26T00:00:00.139Z <Rule:5:Rule.js:697> Rule#rule-kljbrk9g (Schedule - Lawn Lights OFF) evaluate() acquiring mutex 2021-02-26T00:00:00.141Z <Rule:5:Rule.js:700> Rule#rule-kljc5802.evaluate() mutex acquired, evaluating 2021-02-26T00:00:00.145Z <Rule:5:Rule.js:704> Rule#rule-kljc5802 update rate is 0/min limit 60/min 2021-02-26T00:00:00.147Z <Rule:5:Rule.js:654> Rule#rule-kljc5802 evaluateExpressions() with 0 expressions 2021-02-26T00:00:00.150Z <Rule:null> Rule#rule-kljc5802 cond cond57lqecd trange after sdt=2/26/2021, 23:55:00 edt=2/26/2021, 00:00:00 now=2/26/2021, 00:00:00 2021-02-26T00:00:00.152Z <Rule:null> Rule#rule-kljc5802 cond cond57lqecd timer now scheduled for 2/26/2021, 23:55:00, 86099 secs from now 2021-02-26T00:00:00.154Z <Rule:5:Rule.js:714> Rule#rule-kljc5802.evaluate() trigger state false (was false)2021-02-26T11:02:14.128Z <Rule:NOTICE> Rule#rule-kljc5802 configuration changed; reloading 2021-02-26T11:02:14.147Z <Rule:5:Rule.js:600> Rule#rule-kljc5802 reloading with new data 2021-02-26T11:02:14.150Z <Rule:NOTICE> Rule#rule-kljc5802 stopping rule 2021-02-26T11:02:14.152Z <Rule:5:Rule.js:581> Rule#rule-kljc5802 acquiring mutex 2021-02-26T11:02:14.157Z <Rule:5:Rule.js:584> Rule#rule-kljc5802 mutex acquired; unsubscribing from condition dependencies 2021-02-26T11:02:14.169Z <Rule:5:Rule.js:586> Rule#rule-kljc5802 saving states 2021-02-26T11:02:14.176Z <Rule:5:Rule.js:590> Rule#rule-kljc5802 stopped 2021-02-26T11:02:14.178Z <Rule:NOTICE> Rule Rule#rule-kljc5802 stopped 2021-02-26T11:02:14.180Z <Rule:5:Rule.js:555> Rule#rule-kljc5802 start(), awaiting mutex 2021-02-26T11:02:14.183Z <Rule:5:Rule.js:563> Rule#rule-kljc5802 restored states: trig=false, rule=false 2021-02-26T11:02:14.185Z <Rule:5:Rule.js:563> Rule#rule-kljc5802 subscribing to dependencies 2021-02-26T11:02:14.378Z <Rule:INFO> Rule#rule-kljc5802 (Schedule - Festoon Lights OFF) started 2021-02-26T11:02:14.381Z <Rule:5:Rule.js:567> Rule#rule-kljc5802 start() dependencies resolved, performing initial evaluation 2021-02-26T11:02:14.509Z <Rule:5:Rule.js:697> Rule#rule-kljc5802 (Schedule - Festoon Lights OFF) evaluate() acquiring mutex 2021-02-26T11:02:14.511Z <Rule:5:Rule.js:700> Rule#rule-kljc5802.evaluate() mutex acquired, evaluating 2021-02-26T11:02:14.518Z <Rule:5:Rule.js:704> Rule#rule-kljc5802 update rate is 0/min limit 60/min 2021-02-26T11:02:14.520Z <Rule:5:Rule.js:654> Rule#rule-kljc5802 evaluateExpressions() with 0 expressions 2021-02-26T11:02:14.523Z <Rule:null> Rule#rule-kljc5802 cond cond57lqecd trange after sdt=2/26/2021, 23:55:00 edt=2/26/2021, 11:02:00 now=2/26/2021, 11:02:14 2021-02-26T11:02:14.527Z <Rule:null> Rule#rule-kljc5802 cond cond57lqecd timer now scheduled for 2/26/2021, 23:55:00, 46365 secs from now 2021-02-26T11:02:14.529Z <Rule:5:Rule.js:714> Rule#rule-kljc5802.evaluate() trigger state false (was false) 2021-02-26T11:02:52.786Z <Rule:NOTICE> Rule#rule-kljc5802 configuration changed; reloading 2021-02-26T11:02:52.792Z <Rule:5:Rule.js:600> Rule#rule-kljc5802 reloading with new data 2021-02-26T11:02:52.794Z <Rule:NOTICE> Rule#rule-kljc5802 stopping rule 2021-02-26T11:02:52.797Z <Rule:5:Rule.js:581> Rule#rule-kljc5802 acquiring mutex 2021-02-26T11:02:52.803Z <Rule:5:Rule.js:584> Rule#rule-kljc5802 mutex acquired; unsubscribing from condition dependencies 2021-02-26T11:02:52.816Z <Rule:5:Rule.js:586> Rule#rule-kljc5802 saving states 2021-02-26T11:02:52.823Z <Rule:5:Rule.js:590> Rule#rule-kljc5802 stopped 2021-02-26T11:02:52.824Z <Rule:NOTICE> Rule Rule#rule-kljc5802 stopped 2021-02-26T11:02:52.828Z <Rule:5:Rule.js:555> Rule#rule-kljc5802 start(), awaiting mutex 2021-02-26T11:02:52.831Z <Rule:5:Rule.js:563> Rule#rule-kljc5802 restored states: trig=false, rule=false 2021-02-26T11:02:52.833Z <Rule:5:Rule.js:563> Rule#rule-kljc5802 subscribing to dependencies 2021-02-26T11:02:52.835Z <Rule:INFO> Rule#rule-kljc5802 (Schedule - Festoon Lights OFF) started 2021-02-26T11:02:52.838Z <Rule:5:Rule.js:567> Rule#rule-kljc5802 start() dependencies resolved, performing initial evaluation 2021-02-26T11:02:52.840Z <Rule:5:Rule.js:697> Rule#rule-kljc5802 (Schedule - Festoon Lights OFF) evaluate() acquiring mutex 2021-02-26T11:02:52.844Z <Rule:5:Rule.js:700> Rule#rule-kljc5802.evaluate() mutex acquired, evaluating 2021-02-26T11:02:52.846Z <Rule:5:Rule.js:704> Rule#rule-kljc5802 update rate is 1/min limit 60/min 2021-02-26T11:02:52.848Z <Rule:5:Rule.js:654> Rule#rule-kljc5802 evaluateExpressions() with 0 expressions 2021-02-26T11:02:52.850Z <Rule:null> Rule#rule-kljc5802 cond cond57lqecd trange after sdt=2/26/2021, 23:55:00 edt=2/26/2021, 11:02:00 now=2/26/2021, 11:02:52 2021-02-26T11:02:52.852Z <Rule:null> Rule#rule-kljc5802 cond cond57lqecd timer now scheduled for 2/26/2021, 23:55:00, 46327 secs from now 2021-02-26T11:02:52.854Z <Rule:5:Rule.js:714> Rule#rule-kljc5802.evaluate() trigger state false (was false) 2021-02-26T11:03:25.898Z <Rule:NOTICE> Rule#rule-kljc5802 configuration changed; reloading 2021-02-26T11:03:25.904Z <Rule:5:Rule.js:600> Rule#rule-kljc5802 reloading with new data 2021-02-26T11:03:25.905Z <Rule:NOTICE> Rule#rule-kljc5802 stopping rule 2021-02-26T11:03:25.908Z <Rule:5:Rule.js:581> Rule#rule-kljc5802 acquiring mutex 2021-02-26T11:03:25.913Z <Rule:5:Rule.js:584> Rule#rule-kljc5802 mutex acquired; unsubscribing from condition dependencies 2021-02-26T11:03:25.922Z <Rule:5:Rule.js:586> Rule#rule-kljc5802 saving states 2021-02-26T11:03:25.929Z <Rule:5:Rule.js:590> Rule#rule-kljc5802 stopped 2021-02-26T11:03:25.930Z <Rule:NOTICE> Rule Rule#rule-kljc5802 stopped 2021-02-26T11:03:25.933Z <Rule:5:Rule.js:555> Rule#rule-kljc5802 start(), awaiting mutex 2021-02-26T11:03:25.935Z <Rule:5:Rule.js:563> Rule#rule-kljc5802 restored states: trig=false, rule=false 2021-02-26T11:03:25.937Z <Rule:5:Rule.js:563> Rule#rule-kljc5802 subscribing to dependencies 2021-02-26T11:03:25.938Z <Rule:INFO> Rule#rule-kljc5802 (Schedule - Festoon Lights OFF) started 2021-02-26T11:03:25.940Z <Rule:5:Rule.js:567> Rule#rule-kljc5802 start() dependencies resolved, performing initial evaluation 2021-02-26T11:03:25.942Z <Rule:5:Rule.js:697> Rule#rule-kljc5802 (Schedule - Festoon Lights OFF) evaluate() acquiring mutex 2021-02-26T11:03:25.944Z <Rule:5:Rule.js:700> Rule#rule-kljc5802.evaluate() mutex acquired, evaluating 2021-02-26T11:03:25.945Z <Rule:5:Rule.js:704> Rule#rule-kljc5802 update rate is 1/min limit 60/min 2021-02-26T11:03:25.948Z <Rule:5:Rule.js:654> Rule#rule-kljc5802 evaluateExpressions() with 0 expressions 2021-02-26T11:03:25.950Z <Rule:null> Rule#rule-kljc5802 cond cond57lqecd trange after sdt=2/26/2021, 23:55:00 edt=2/26/2021, 11:03:00 now=2/26/2021, 11:03:25 2021-02-26T11:03:25.952Z <Rule:null> Rule#rule-kljc5802 cond cond57lqecd timer now scheduled for 2/26/2021, 23:55:00, 46294 secs from now 2021-02-26T11:03:25.954Z <Rule:5:Rule.js:714> Rule#rule-kljc5802.evaluate() trigger state false (was false) 2021-02-26T11:03:52.673Z <Rule:NOTICE> Rule#rule-kljc5802 configuration changed; reloading 2021-02-26T11:03:52.677Z <Rule:5:Rule.js:600> Rule#rule-kljc5802 reloading with new data 2021-02-26T11:03:52.693Z <Rule:NOTICE> Rule#rule-kljc5802 stopping rule 2021-02-26T11:03:52.695Z <Rule:5:Rule.js:581> Rule#rule-kljc5802 acquiring mutex 2021-02-26T11:03:52.701Z <Rule:5:Rule.js:584> Rule#rule-kljc5802 mutex acquired; unsubscribing from condition dependencies 2021-02-26T11:03:52.721Z <Rule:5:Rule.js:586> Rule#rule-kljc5802 saving states 2021-02-26T11:03:52.729Z <Rule:5:Rule.js:590> Rule#rule-kljc5802 stopped 2021-02-26T11:03:52.731Z <Rule:NOTICE> Rule Rule#rule-kljc5802 stopped 2021-02-26T11:03:52.733Z <Rule:5:Rule.js:555> Rule#rule-kljc5802 start(), awaiting mutex 2021-02-26T11:03:52.736Z <Rule:5:Rule.js:563> Rule#rule-kljc5802 restored states: trig=false, rule=false 2021-02-26T11:03:52.738Z <Rule:5:Rule.js:563> Rule#rule-kljc5802 subscribing to dependencies 2021-02-26T11:03:52.740Z <Rule:INFO> Rule#rule-kljc5802 (Schedule - Festoon Lights OFF) started 2021-02-26T11:03:52.742Z <Rule:5:Rule.js:567> Rule#rule-kljc5802 start() dependencies resolved, performing initial evaluation 2021-02-26T11:03:52.744Z <Rule:5:Rule.js:697> Rule#rule-kljc5802 (Schedule - Festoon Lights OFF) evaluate() acquiring mutex 2021-02-26T11:03:52.747Z <Rule:5:Rule.js:700> Rule#rule-kljc5802.evaluate() mutex acquired, evaluating 2021-02-26T11:03:52.749Z <Rule:5:Rule.js:704> Rule#rule-kljc5802 update rate is 1/min limit 60/min 2021-02-26T11:03:52.754Z <Rule:5:Rule.js:654> Rule#rule-kljc5802 evaluateExpressions() with 0 expressions 2021-02-26T11:03:52.757Z <Rule:null> Rule#rule-kljc5802 cond cond57lqecd trange after sdt=2/26/2021, 23:55:00 edt=2/26/2021, 11:03:00 now=2/26/2021, 11:03:52 2021-02-26T11:03:52.759Z <Rule:null> Rule#rule-kljc5802 cond cond57lqecd timer now scheduled for 2/26/2021, 23:55:00, 46267 secs from now 2021-02-26T11:03:52.761Z <Rule:5:Rule.js:714> Rule#rule-kljc5802.evaluate() trigger state false (was false) 2021-02-26T11:04:13.259Z <Rule:NOTICE> Rule#rule-kljc5802 configuration changed; reloading 2021-02-26T11:04:13.264Z <Rule:5:Rule.js:600> Rule#rule-kljc5802 reloading with new data 2021-02-26T11:04:13.265Z <Rule:NOTICE> Rule#rule-kljc5802 stopping rule 2021-02-26T11:04:13.266Z <Rule:5:Rule.js:581> Rule#rule-kljc5802 acquiring mutex 2021-02-26T11:04:13.271Z <Rule:5:Rule.js:584> Rule#rule-kljc5802 mutex acquired; unsubscribing from condition dependencies 2021-02-26T11:04:13.274Z <Rule:5:Rule.js:586> Rule#rule-kljc5802 saving states 2021-02-26T11:04:13.281Z <Rule:5:Rule.js:590> Rule#rule-kljc5802 stopped 2021-02-26T11:04:13.282Z <Rule:NOTICE> Rule Rule#rule-kljc5802 stopped 2021-02-26T11:04:13.284Z <Rule:5:Rule.js:555> Rule#rule-kljc5802 start(), awaiting mutex 2021-02-26T11:04:13.286Z <Rule:5:Rule.js:563> Rule#rule-kljc5802 restored states: trig=false, rule=false 2021-02-26T11:04:13.287Z <Rule:5:Rule.js:563> Rule#rule-kljc5802 subscribing to dependencies 2021-02-26T11:04:13.289Z <Rule:INFO> Rule#rule-kljc5802 (Schedule - Festoon Lights OFF) started 2021-02-26T11:04:13.290Z <Rule:5:Rule.js:567> Rule#rule-kljc5802 start() dependencies resolved, performing initial evaluation 2021-02-26T11:04:13.292Z <Rule:5:Rule.js:697> Rule#rule-kljc5802 (Schedule - Festoon Lights OFF) evaluate() acquiring mutex 2021-02-26T11:04:13.293Z <Rule:5:Rule.js:700> Rule#rule-kljc5802.evaluate() mutex acquired, evaluating 2021-02-26T11:04:13.295Z <Rule:5:Rule.js:704> Rule#rule-kljc5802 update rate is 2/min limit 60/min 2021-02-26T11:04:13.297Z <Rule:5:Rule.js:654> Rule#rule-kljc5802 evaluateExpressions() with 0 expressions 2021-02-26T11:04:13.299Z <Rule:null> Rule#rule-kljc5802 cond cond57lqecd trange after sdt=2/26/2021, 23:55:00 edt=2/26/2021, 11:04:00 now=2/26/2021, 11:04:13 2021-02-26T11:04:13.300Z <Rule:null> Rule#rule-kljc5802 cond cond57lqecd timer now scheduled for 2/26/2021, 23:55:00, 46246 secs from now 2021-02-26T11:04:13.302Z <Rule:5:Rule.js:714> Rule#rule-kljc5802.evaluate() trigger state false (was false)2021-02-26T11:04:15.369Z <Rule:5:Rule.js:700> Rule#rule-kljc5802.evaluate() mutex acquired, evaluating 2021-02-26T11:04:15.371Z <Rule:5:Rule.js:704> Rule#rule-kljc5802 update rate is 3/min limit 60/min 2021-02-26T11:04:15.373Z <Rule:5:Rule.js:654> Rule#rule-kljc5802 evaluateExpressions() with 0 expressions 2021-02-26T11:04:15.375Z <Rule:null> Rule#rule-kljc5802 cond cond57lqecd trange after sdt=2/26/2021, 23:55:00 edt=2/26/2021, 11:04:00 now=2/26/2021, 11:04:15 2021-02-26T11:04:15.377Z <Rule:null> Rule#rule-kljc5802 cond cond57lqecd timer now scheduled for 2/26/2021, 23:55:00, 46244 secs from now 2021-02-26T11:04:15.379Z <Rule:5:Rule.js:714> Rule#rule-kljc5802.evaluate() trigger state false (was false)2021-02-26T11:18:29.114Z <Rule:5:Rule.js:680> Rule#rule-kljc5802.evaluate() mutex acquired, evaluating 2021-02-26T11:18:29.117Z <Rule:5:Rule.js:684> Rule#rule-kljc5802 update rate is 1/min limit 60/min 2021-02-26T11:18:29.119Z <Rule:5:Rule.js:634> Rule#rule-kljc5802 evaluateExpressions() with 0 expressions 2021-02-26T11:18:29.124Z <Rule:null> Rule#rule-kljc5802 cond cond57lqecd trange after sdt=2/26/2021, 23:55:00 edt=2/26/2021, 11:18:00 now=2/26/2021, 11:18:29 2021-02-26T11:18:29.127Z <Rule:null> Rule#rule-kljc5802 cond cond57lqecd timer now scheduled for 2/26/2021, 23:55:00, 45390 secs from now 2021-02-26T11:18:29.130Z <Rule:5:Rule.js:694> Rule#rule-kljc5802.evaluate() trigger state false (was false) -
Grep'ing out specific lines of the log isn't really a productive thing to do, as there are other lines surrounding in context that may not contain the search string but are needed to show the full activity. It would not, for example, show an exception thrown. Just gzip the log and email it to me at the address given in the "SUPPORT" section of the about page; I'll take a look later this morning.
Not related but I am seeing these errors in the log:
Expression compilation error for deviceclass heatonly_thermostat hvac_control.mode: Error: Parse error on line 1: ...tochangeover:'auto'}[lower(value)] ?? vaDevice 190 is the Secure Boiler Relay Switch related to the Secure Thermostat device.
2021-02-25T18:03:47.240Z <VeraController:ERR> Exception/error while updating Entity#vera>device_190 2021-02-25T18:03:47.242Z <VeraController:CRIT> ReferenceError: expr is not defined ReferenceError: expr is not defined -
Are you in 21056?
Are you in 21056?
@toggledbits Yes
Two more rules here both are set to run at 9am
One worked this morning OK and did its action, the other rule the bottom one in the screen shot, that didn't run its action.
This is the rule that didn't run, have I done something wrong ?
I've just updated to the latest version of MSR (reactor-0.1.21057-f143fd3-generic.tar) and now that rule that didn't run this morning looks like this:
I have created a lot of other rules, some of them also with Constraints and none of those rules say null or no data in the Constraints in the rules summary card.
I've gone through them all now again looking and it seems I only have two rules which I have highlighted above that don't run and they say or have said null or no data in Constraints.
All my other garden lights have turned on and off OK, but they are using a sunset offset not a specific set time.
But that rule to turn off the Festoon lights at 23:55pm has never run since I created it.
I also have rules for the window coverings setup for specific times in the morning and generally they have all run at their set times OK.
I will see what happens tomorrow at 9am with this "Lounge Blind Slats" one ?
The 11:55pm rule that never worked since I created it, I deleted it. I then created it again exactly the same as I did before. Looking at its Summary card the Constraints stated no data / null etc. I then edited the rule and changed its time to 9:00am and saved. I then edited the rule again and set it back to 11:55pm and saved.
The rule now runs and turns off my lights at 11:55pm or it did last night at least anyway. So assume it will work every night now.
I created another new rule not related to run every night at 10:30pm and that one worked first time no problems, so not sure why I have had issues with a few rules.
The 9am rule to open the Lounge Blind Slats didn't run this morning again, so I've deleted it and recreated it, see what happens with that tomorrow morning ?
Remember two things:
- Log files are pretty good at telling what's going on, and really good at help me determine what's going on;
- Open PRs are my highest priority.
OK. Not seeing an email yet... you used the address in the "Support" section of the About page?