Reactor build 26116: empty group reaction
therealdbT
I have a couple of rules that has group reactions with empty conditions. I notice, in particular on one that's called every 5 secs, that it was not working. I added an empty comment as condition and it started working again. I don't know if saving was enough to "reset" it, but I'm reporting anyway. No errors in the logs, but the MQTT message was not published, so I had an easy path to check the rule. I have others like these, but not easy to test. @toggledbits maybe some stuck status data? (I restarted a couple of times after the last update). Thanks.
Multi-System Reactor
Reactor (Multi-System/Multi-Hub) Announcements
toggledbitsT
Build 21228 has been released. Docker images available from DockerHub as usual, and bare-metal packages here. Home Assistant up to version 2021.8.6 supported; the online version of the manual will now state the current supported versions; Fix an error in OWMWeatherController that could cause it to stop updating; Unify the approach to entity filtering on all hub interface classes (controllers); this works for device entities only; it may be extended to other entities later; Improve error detail in messages for EzloController during auth phase; Add isRuleSet() and isRuleEnabled() functions to expressions extensions; Implement set action for lock and passage capabilities (makes them more easily scriptable in some cases); Fix a place in the UI where 24-hour time was not being displayed.
Multi-System Reactor
Upcoming Storage Change -- Got Back-ups?
toggledbitsT
TL;DR: Format of data in storage directory will soon change. Make sure you are backing up the contents of that directory in its entirety, and you preserve your backups for an extended period, particularly the backup you take right before upgrading to the build containing this change (date of that is still to be determined, but soon). The old data format will remain readable (so you'll be able to read your pre-change backups) for the foreseeable future. In support of a number of other changes in the works, I have found it necessary to change the storage format for Reactor objects in storage at the physical level. Until now, plain, standard JSON has been used to store the data (everything under the storage directory). This has served well, but has a few limitations, including no real support for native JavaScript objects like Date, Map, Set, and others. It also is unable to store data that contains "loops" — objects that reference themselves in some way. I'm not sure exactly when, but in the not-too-distant future I will publish a build using the new data format. It will automatically convert existing JSON data to the new format. For the moment, it will save data in both the new format and the old JSON format, preferring the former when loading data from storage. I have been running my own home with this new format for several months, and have no issues with data loss or corruption. A few other things to know: If you are not already backing up your storage directory, you should be. At a minimum, back this directory up every time you make big changes to your Rules, Reactions, etc. Your existing JSON-format backups will continue to be readable for the long-term (years). The code that loads data from these files looks for the new file format first (which will have a .dval suffix), and if not found, will happily read (and convert) a same-basenamed .json file (i.e. it looks for ruleid.dval first, and if it doesn't find it, it tries to load ruleid.json). I'll publish detailed instructions for restoring from old backups when the build is posted (it's easy). The new .dval files are not directly human-readable or editable as easily as the old .json files. A new utility will be provided in the tools directory to convert .dval data to .json format, which you can then read or edit if you find that necessary. However, that may not work for all future data, as my intent is to make more native JavaScript objects directly storable, and many of those objects cannot be stored in JSON. You may need to modify your backup tools/scripts to pick up the new files: if you explicitly name .json files (rather than just specifying the entire storage directory) in your backup configuration, you will need to add .dval files to get a complete, accurate backup. I don't think this will be an issue for any of you; I imagine that you're all just backing up the entire contents of storage regardless of format/name, that is the safest (and IMO most correct) way to go (if that's not what you're doing, consider changing your approach). The current code stores the data in both the .dval form and the .json form to hedge against any real-world problems I don't encounter in my own use. Some future build will drop this redundancy (i.e. save only to .dval form). However, the read code for the .json form will remain in any case. This applies only to persistent storage that Reactor creates and controls under the storage tree. All other JSON data files (e.g. device data for Controllers) are unaffected by this change and will remain in that form. YAML files are also unaffected by this change. This thread is open for any questions or concerns.
Multi-System Reactor
Next Release?
CatmanV2C
Morning. Do we have a roadmap for the next release, at all? I only ask as there's a breaking HA change and I have many packages now out of date. Cheers! C
Multi-System Reactor
Controller Z-Wave JS UI: "Location" attribute not visible in Reactor entities
N
Hi, I'm on Docker/NAs (latest-26011-c621bbc7) with Zwave js ui (last version). I have set the 'Location' for each device in the Z-Wave JS UI dashboard, I cannot find this information among the Entity Attributes in the Reactor. I tried and the result is an empty array []. It seems the 'Location' metadata from Z-Wave JS is not being mapped to a standard attribute in Reactor. Location is equale to Rooms for me. When comparing this to the Vera or Ezlo Controller, Reactor automatically creates Room Icons also in the Reactor Dashboard and places the various devices under those room categories. This is a very convenient way to keep the dashboard organized and quickly find lights to turn off with a click (especially when something isn't switched off as expected for me:) ). Is there a way to map the Z-Wave JS UI 'Location' attribute and a dashboard organization, just like it does with Vera/Ezlo? Thanks in advance for all the great tips you've shared
Multi-System Reactor
Variables not updating properly
tunnusT
Topic thumbnail image
Multi-System Reactor
[Solved] Loading Screen Safari
S
Topic thumbnail image
Multi-System Reactor
VEC Virtual Switch Auto Off
S
I use Virtual Entity Controller virtual switches which I turn on via webhooks from other applications. Once a switch triggers and turns on, I can then activate associated rules. I would like each virtual switch to automatically turn off after a configurable time (e.g., 5 seconds, 10 seconds). Is there a better way to achieve this auto-off behavior instead of creating a separate rule for each switch that uses the 'Condition must be sustained for' option to turn it off? With a large number of these switches (and the associated turn-off rules), I'm checking to see if there is a simpler approach.If not, could this be a feature request to add an auto-off timer directly to the virtual switches. Thanks Reactor (Multi-hub) latest-26011-c621bbc7 VirtualEntityController v25356 Synology Docker
Multi-System Reactor
Changes operator does not always detect change
tunnusT
I've had similar problems before, but now this issue has resurfaced. Using build 26011 on Docker. As I copied one old rule as a "template" for a similar new rule, where I have multiple conditions using changes operator (from any to any, and with delay reset of 900), these conditions do not detect change in attributes. Even if I manually reset the rule, reset delay timers do not restart. If I do a new rule from scratch, and do not copy/import anything old, the same conditions work properly. Also, if I modify copied rule's conditions (put a random number to "from" & "to" fields), then save, and after that remove those modifications, rule begins to function normally. Just editing e.g. delay reset value does not do any good in this context. @toggledbits, I can DM logs & related rule files to you, if you just send me instructions.
Multi-System Reactor
Dynamic MQTT topics and parameters
M
Topic thumbnail image
Multi-System Reactor
Condition for trend
T
Topic thumbnail image
Multi-System Reactor
Struggling to setup my first Tasmota device and MQTT
cw-kidC
Topic thumbnail image
Multi-System Reactor
Existing Rule stopped working HTTP command fetching IP address from website
cw-kidC
Topic thumbnail image
Multi-System Reactor
Set reaction triggering wrong z-wave device
T
Topic thumbnail image
Multi-System Reactor
Can you run MSR on Home Assistant OS ?
cw-kidC
Looking at using Home Assistant for the first time, either on a Home Assistant Green, their own hardware or buying a cheap second hand mini PC. Sounds like Home Assistant OS is linux based using Docker for HA etc. Would I also be able to install things like MSR as well on their OS ? On the same box? Thanks.
Multi-System Reactor
How to upgrade from an old version of MSR?
cw-kidC
Hello I haven't updated my installation of MSR in a very long time. Its a bare metal Linux install currently on version 24366-3de60836 I see the latest version is now latest-26011-c621bbc7 I assume I cannot just jump from a very old version to the latest version? Or can I? Thanks
Multi-System Reactor
This trigger no longer working - complaining about the operator needing changing
cw-kidC
Topic thumbnail image
Multi-System Reactor
Self test
CatmanV2C
Having been messing around with some stuff I worked a way to self trigger some tests that I wanted to do on the HA <> MSR integration This got me wondering if there's an entity that changes state / is exposed when a configured controller goes off line? I can't see one but thought it might be hidden or something? Cheers C
Multi-System Reactor
Access control - allowing anonymous user to dashboard
tunnusT
Using build 25328 and having the following users.yaml configuration: users: # This section defines your valid users. admin: ******* groups: # This section defines your user groups. Optionally, it defines application # and API access restrictions (ACLs) for the group. Users may belong to # more than one group. Again, no required or special groups here. admin_group: users: - admin applications: true # special form allows access to ALL applications guests: users: "*" applications: - dashboard api_acls: # This ACL allows users in the "admin" group to access the API - url: "/api" group: admin_group allow: true log: true # This ACL allows anyone/thing to access the /api/v1/alive API endpoint - url: "/api/v1/alive" allow: true session: timeout: 7200 # (seconds) rolling: true # activity extends timeout when true # If log_acls is true, the selected ACL for every API access is logged. log_acls: true # If debug_acls is true, even more information about ACL selection is logged. debug_acls: true My goal is to allow anonymous user to dashboard, but MSR is still asking for a password when trying to access that. Nothing in the logs related to dashboard access. Probably an error in the configuration, but help needed to find that. Tried to put url: "/dashboard" under api_acls, but that was a long shot and didn't work.
Multi-System Reactor
Oddness in Copy/Move of Reactions
G
Topic thumbnail image
Multi-System Reactor

Condition for trend

Scheduled Pinned Locked Moved Multi-System Reactor
12 Posts 2 Posters 719 Views 2 Watching
  • Oldest to Newest
  • Newest to Oldest
  • Most Votes
Reply
  • Reply as topic
Log in to reply
This topic has been deleted. Only users with topic management privileges can see it.
  • T Offline
    T Offline
    tamorgen
    wrote on last edited by tamorgen
    #1

    Is there a way to set a condition for a trending number? I just installed a Zooz ZSE44 Temp/Humidity sensor in one of my bathrooms. I wanted to set a condition based upon how quickly the Humidity sensor reports the humidity level trending down (say after a shower).

    If you look at the graph below from the device, you can see the humidity spiking at 5 am, then dropping, then spiking again, then dropping. I'm trying to set up a condition when the level trends up or down quickly.

    63f41559-2267-4c71-8530-928ab6bc0862-image.png

    1 Reply Last reply
    0
    • T Offline
      T Offline
      tamorgen
      wrote on last edited by
      #2

      I think I may have figured out a way...

      If I use a Latch condition when the Humidity goes above 60, and then another condition when it goes below 45 (dependent on the first condition being true first), that should give me the result I'm looking for; that being the shower isn't being used anymore, and the shower light can be turned off. Am I correct in my understanding of how Latch works, in that that condition will stay true until the Set Reaction triggers?

      e1783236-b56f-4b4f-b16e-62d304c5b3a3-image.png

      1 Reply Last reply
      0
      • toggledbitsT Offline
        toggledbitsT Offline
        toggledbits
        wrote on last edited by
        #3

        VirtualEntityController can sample another entity's data and do time-series aggregation (moving average, rate of change, etc.).

        Refer to the documentation for VirtualEntityController

        Author of Multi-system Reactor and Reactor, DelayLight, Switchboard, and about a dozen other plugins that run on Vera and openLuup.

        T 1 Reply Last reply
        0
        • toggledbitsT toggledbits

          VirtualEntityController can sample another entity's data and do time-series aggregation (moving average, rate of change, etc.).

          Refer to the documentation for VirtualEntityController

          T Offline
          T Offline
          tamorgen
          wrote on last edited by
          #4

          @toggledbits said in Condition for trend:

          VirtualEntityController can sample another entity's data and do time-series aggregation (moving average, rate of change, etc.).

          Thanks for that. I wasn't familiar with that, and it sounds like what I was initially looking for.

          1 Reply Last reply
          0
          • T Offline
            T Offline
            tamorgen
            wrote on last edited by tamorgen
            #5

            So, for some reason, my Latch method isn't working. I see the humidity go above 70, and I see the first condition go true. When I'm done showering, and fan evacuates the excess humidity, it drops back down and goes below 65, and that condition becomes true.

            The second condition has the restriction that it must occur after the first condition is met.

            I guess the second condition resets the Latched condition, so both conditions aren't true at the same time?

            Is there another way to do a first condition, then the second condition that I'm missing?

            a1e59054-aeba-4f64-9c59-1206fdc0855b-image.png

            toggledbitsT 1 Reply Last reply
            0
            • T tamorgen

              So, for some reason, my Latch method isn't working. I see the humidity go above 70, and I see the first condition go true. When I'm done showering, and fan evacuates the excess humidity, it drops back down and goes below 65, and that condition becomes true.

              The second condition has the restriction that it must occur after the first condition is met.

              I guess the second condition resets the Latched condition, so both conditions aren't true at the same time?

              Is there another way to do a first condition, then the second condition that I'm missing?

              a1e59054-aeba-4f64-9c59-1206fdc0855b-image.png

              toggledbitsT Offline
              toggledbitsT Offline
              toggledbits
              wrote on last edited by
              #6

              @tamorgen said in Condition for trend:

              I guess the second condition resets the Latched condition, so both conditions aren't true at the same time?

              Correct. Both conditions cannot be true at the same time.

              Your relatively simple logic here doesn't need a latch. Just use two rules, one to turn the fan on at humidity >= 70, and the other to turn it off when humidity <= 65.

              If you insist on a latch in one rule, then you need to pair the latching condition with a condition that stays true until it's time to reset it. Really, all you need to do is reverse the operand in your second condition: it should be humidity >= 65 (and this second condition not latching). When humidity rises, the second condition will go true before the first (latching) condition, but won't Set the rule because both must be true. When the humidity gets to 70, the first will go true, so both will then be true, and the Set Reaction then runs to turn the fan on. As humidity comes down below 70, the first condition will become logically false, but remain in true state because it is latched while the second condition also remains true (i.e. humidity hasn't yet reached the low cutoff). When the humidity drops below 65, the second condition will go false, causing the reset of the latch on the first condition. The Reset Reaction then runs (it turns the fan off).

              That said, seasonally and with local changes in weather, your indoor humidity varies, and using fixed values like this may not work out very well over the course of a year. I've tried. That's why I added aggregates/trending to VirtualEntityController. You can have VEC create a rate aggregate over 5 minutes. You'd need to "tune" the condition's rate value test, but as a starting point for the conditions, let's say if the rate of change exceeds 2.0 (which is % humidity per minute, the unit VEC will report for rate, equating to about 10% (positive) change in the five minute sampling period), your rule turns the fan on. It may be a little trickier figuring out when to turn the fan off. As a practical matter, I've found that having the fan run on a timed basis for 30 minutes once triggered is a simplifying assumption that works out perfectly in my bathroom, but you could also look at rate (e.g. rate of change is <0.0167 sustained for 15 minutes, for example). I would always add a time component to the run of exhaust fans in any case, because these simple fans aren't built for long runtimes (bathroom exhaust fans have started fires from running too long).

              controllers:
              - id: virtual
                enabled: true
                implementation: VirtualEntityController
                name: Virtual Entity Controller
                config:
                  entities:
                    - id: "master_bath_rh_rate"
                      name: "Master Bath Humidity Change Rate"
                      type: ValueSensor
                      capabilities:
                        value_sensor:
                          attributes:
                            value:
                              model: time series
                              aggregate: rate
                              entity: "mqtt>shelly_handt3"
                              attribute: "humidity_sensor.value"
                              interval: 150
                              retention: 300
                              precision: 3
                      primary_attribute: "value_sensor.value"
              

              Author of Multi-system Reactor and Reactor, DelayLight, Switchboard, and about a dozen other plugins that run on Vera and openLuup.

              1 Reply Last reply
              0
              • T Offline
                T Offline
                tamorgen
                wrote on last edited by
                #7

                Okay, so maybe I'm missing something or not explaining my train of though here....

                First, I'm not trying to control an exhaust fan, I'm trying to control the shower light. The exhaust fan has it's own built in sensor and . I'm using the humidity to determine that someone is taking a shower, so the light should remain on. When someone stops taking a shower, the humidity will drop (due to the automatic exhaust fan), and then the light can be turned off. I can't easily put a motion sensor in the shower, so the humidity sensor is the logical sensor. I've observed the values before, during, and after taking a shower, and generally, the humidity in that room is 30's or 40's, and when a shower is in play, it jumps up to the 70's or 80's.

                4c13271d-1c7e-491e-bb35-c0c11ac2c740-image.png

                I tried doing it with just one rule, but there really isn't a operand to change below a number. There is Changes from x to y, and then < or <=. If I just have a simple rule to say below 65%, then the light will go off before the humidity level rises. This is why I was trying to latch aspect, because generally when I step into the bathroom, I manually turn on the shower light, turn on the shower, finish, and inevitably the shower light get's left on, whether it's me or my wife.

                I initially thought about the trend/time aspect, but I thought that for this purpose, that is actually over complicating things. All I really need to know is a) did the humidity level rise above point A, and b) did it drop below point B, in that sequence.

                So, from my understanding, you are saying I just need to change the value fo the first condition to >= 65, and the second condition can stay at <= 65?

                08b7b9d8-ba28-47b1-bef6-a44bf8d6ca5a-image.png

                toggledbitsT 1 Reply Last reply
                0
                • T tamorgen

                  Okay, so maybe I'm missing something or not explaining my train of though here....

                  First, I'm not trying to control an exhaust fan, I'm trying to control the shower light. The exhaust fan has it's own built in sensor and . I'm using the humidity to determine that someone is taking a shower, so the light should remain on. When someone stops taking a shower, the humidity will drop (due to the automatic exhaust fan), and then the light can be turned off. I can't easily put a motion sensor in the shower, so the humidity sensor is the logical sensor. I've observed the values before, during, and after taking a shower, and generally, the humidity in that room is 30's or 40's, and when a shower is in play, it jumps up to the 70's or 80's.

                  4c13271d-1c7e-491e-bb35-c0c11ac2c740-image.png

                  I tried doing it with just one rule, but there really isn't a operand to change below a number. There is Changes from x to y, and then < or <=. If I just have a simple rule to say below 65%, then the light will go off before the humidity level rises. This is why I was trying to latch aspect, because generally when I step into the bathroom, I manually turn on the shower light, turn on the shower, finish, and inevitably the shower light get's left on, whether it's me or my wife.

                  I initially thought about the trend/time aspect, but I thought that for this purpose, that is actually over complicating things. All I really need to know is a) did the humidity level rise above point A, and b) did it drop below point B, in that sequence.

                  So, from my understanding, you are saying I just need to change the value fo the first condition to >= 65, and the second condition can stay at <= 65?

                  08b7b9d8-ba28-47b1-bef6-a44bf8d6ca5a-image.png

                  toggledbitsT Offline
                  toggledbitsT Offline
                  toggledbits
                  wrote on last edited by toggledbits
                  #8

                  @tamorgen said in Condition for trend:

                  generally when I step into the bathroom, I manually turn on the shower light, turn on the shower, finish, and inevitably the shower light get's left on, whether it's me or my wife.

                  Important detail.

                  @tamorgen said in Condition for trend:

                  So, from my understanding, you are saying I just need to change the value fo the first condition to >= 65, and the second condition can stay at <= 65?

                  No. Both conditions >=, and you should have a deadband between them. And since you turn the light on manually, the Set Reaction in that rule can do nothing, and the Reset Reaction turns the light off.

                  Your image is now mixing concepts and adding condition options not discussed, not needed. Based on your graph and descriptions, I would go with exactly this (do not add any other features) and see how it goes:

                  1. Condition #1: humidity >= 65, latching output
                  2. Condition #2: humidity >= 50, default (follow) output
                  3. Set Reaction: empty
                  4. Reset Reaction: turn light off.

                  Note that both conditions are >=. This is the way.

                  Author of Multi-system Reactor and Reactor, DelayLight, Switchboard, and about a dozen other plugins that run on Vera and openLuup.

                  1 Reply Last reply
                  0
                  • T Offline
                    T Offline
                    tamorgen
                    wrote on last edited by
                    #9

                    Okay, thank you. That makes sense…. Other than deadband. What do you mean by that?

                    1 Reply Last reply
                    0
                    • toggledbitsT Offline
                      toggledbitsT Offline
                      toggledbits
                      wrote on last edited by toggledbits
                      #10

                      Deadband... a range of the measurement where nothing happens; but there is usually action at the extremes of the deadband (the low and high values).

                      With the configuration I gave you, it's the range of humidity between 50% and 65%... if the humidity goes only from 40% to 55%, that 55% is in the "deadband" and the rule won't turn the light off if the humidity then falls below 50% (the low end of the deadband) because the humidity never exceeded the high end (65%) of the deadband. But the way the rule is set up, if the humidity does reach 65%, then the rule becomes "sensitive" and watches for the humidity to drop below 50%, and then it will turn the light off.

                      Deadband is also commonly used to refer to thermostats, for example, where it's commonly the small differential enforced between a heating setpoint and a cooling setpoint so that the thermostat won't try to do both at the same time, or bang back and forth between the two rapidly when the temperature is in a small range between those setpoints.

                      Author of Multi-system Reactor and Reactor, DelayLight, Switchboard, and about a dozen other plugins that run on Vera and openLuup.

                      1 Reply Last reply
                      0
                      • T Offline
                        T Offline
                        tamorgen
                        wrote on last edited by
                        #11

                        Okay, I understand. For a minute I thought it there was a setting I needed to enable. I've set it up and I'll know if it works in the morning. Thanks for all the help.

                        T 1 Reply Last reply
                        0
                        • T tamorgen

                          Okay, I understand. For a minute I thought it there was a setting I needed to enable. I've set it up and I'll know if it works in the morning. Thanks for all the help.

                          T Offline
                          T Offline
                          tamorgen
                          wrote on last edited by
                          #12

                          Update. Worked perfectly. Thanks for setting me striaght!

                          1 Reply Last reply
                          1
                          Reply
                          • Reply as topic
                          Log in to reply
                          • Oldest to Newest
                          • Newest to Oldest
                          • Most Votes


                          Recent Topics

                          • Reactor build 26116: empty group reaction
                            therealdbT
                            therealdb
                            0
                            1
                            11

                          • Reactor (Multi-System/Multi-Hub) Announcements
                            toggledbitsT
                            toggledbits
                            5
                            134
                            97.3k

                          • Temperature control with TRVs
                            CatmanV2C
                            CatmanV2
                            0
                            1
                            79

                          • Upcoming Storage Change -- Got Back-ups?
                            toggledbitsT
                            toggledbits
                            3
                            2
                            294

                          • Next Release?
                            CatmanV2C
                            CatmanV2
                            0
                            6
                            278

                          • Controller Z-Wave JS UI: "Location" attribute not visible in Reactor entities
                            toggledbitsT
                            toggledbits
                            0
                            2
                            192

                          • Do you Matter?
                            CrilleC
                            Crille
                            0
                            8
                            972

                          • Variables not updating properly
                            tunnusT
                            tunnus
                            0
                            5
                            275

                          • [Solved] Loading Screen Safari
                            S
                            SweetGenius
                            0
                            11
                            1.1k

                          • VEC Virtual Switch Auto Off
                            S
                            SweetGenius
                            1
                            2
                            320

                          • Changes operator does not always detect change
                            toggledbitsT
                            toggledbits
                            0
                            4
                            345

                          • Dynamic MQTT topics and parameters
                            M
                            mgvra
                            0
                            6
                            473
                          Powered by NodeBB | Contributors
                          Hosted freely by 10RUPTiV - Solutions Technologiques | Contact us
                          • Login

                          • Don't have an account? Register

                          • Login or register to search.
                          • First post
                            Last post
                          0
                          • Categories
                          • Recent
                          • Tags
                          • Popular
                          • Unsolved