  4. Sending numbers as payload type in actions enhancement
4 Posts 2 Posters 955 Views 2 Watching
  • J Offline
    J Offline
    jouke
    wrote on last edited by jouke
    I'm controlling a HVAC device through the MQTTController. While setting up the entity config in reactor.yaml, I started with this on the action block:
                  set_setpoint:
                    topic: "ezlo_mqtt/set/item/%topic%/set/Tsetpoint"
                    payload:
                      expr: "parameters.setpoint"
                      type: raw
    However, as the setpoint is a number in the UI, things were not fully parseable as a number and nothing was outputted to mqtt.
    So I've added this code to MQTTController.js at line 1449 to add the payload type 'number':
                } else if ( 'number' === act.payload.type ) {
                    payload = String( payload );
                } else if (''raw' !== ( act.payload.type || 'raw' ) ) {
    After this change, I was able to set the payload type to number:
                  set_setpoint:
                    payload:
                      type: number
    And things worked as intended, being able to send numbers in the actions bit of a rule set.
      You can just send it raw, which has the same effect as your (unnecessary) code addition. In fact, you can just send it JSON, too, since a JSON-ified number is just the number as a string, same-same. Alternately, you can also use:
          payload:
            expr: "str(parameters.setpoint)"
      • J Offline
        J Offline
        jouke
        I was expecting raw to work, however using raw throws an error in my reactor.log file:
        [stable-23078]2023-05-16T11:27:22.250Z <MQTTController:WARN> expression has run, result 20
        [stable-23078]2023-05-16T11:27:22.250Z <MQTTController:INFO> MQTTController#mqtt perform hvac_cooling_unit.set_setpoint on MHI_AC_1: publishing ezlo_mqtt/set/item/MHI-AC-Woonkamer/set/Tsetpoint 20
        [stable-23078]2023-05-16T11:27:22.254Z <wsapi:CRIT> TypeError: The "string" argument must be of type string or an instance of Buffer or ArrayBuffer. Received type number (20) [-]
        TypeError [ERR_INVALID_ARG_TYPE]: The "string" argument must be of type string or an instance of Buffer or ArrayBuffer. Received type number (20)
            at new NodeError (node:internal/errors:372:5)
            at Function.byteLength (node:buffer:735:11)
            at publish (/var/reactor/ext/MQTTController/node_modules/mqtt-packet/writeToStream.js:334:51)
            at Object.generate [as writeToStream] (/var/reactor/ext/MQTTController/node_modules/mqtt-packet/writeToStream.js:34:14)
            at sendPacket (/var/reactor/ext/MQTTController/node_modules/mqtt/lib/client.js:176:29)
            at MqttClient._sendPacket (/var/reactor/ext/MQTTController/node_modules/mqtt/lib/client.js:1250:7)
            at publishProc (/var/reactor/ext/MQTTController/node_modules/mqtt/lib/client.js:659:14)
            at MqttClient.publish (/var/reactor/ext/MQTTController/node_modules/mqtt/lib/client.js:665:74)
            at /var/reactor/ext/MQTTController/MQTTController.js:616:25
            at new Promise (<anonymous>)
        As you can see, I try to publish the raw value 20 to topic ezlo/.../Tsetpoint which fails as the number is not a string (so far for untyped behaviour of js..)
        Both your alternatives, using json or raw with the str() expression work flawlessly. I'll remove my unneeded changes in the code!
          OK. I can address the error message. Best of both worlds.