  4. Integrate UPS with MSR
TL;DR: Format of data in storage directory will soon change. Make sure you are backing up the contents of that directory in its entirety, and you preserve your backups for an extended period, particularly the backup you take right before upgrading to the build containing this change (date of that is still to be determined, but soon). The old data format will remain readable (so you'll be able to read your pre-change backups) for the foreseeable future. In support of a number of other changes in the works, I have found it necessary to change the storage format for Reactor objects in storage at the physical level. Until now, plain, standard JSON has been used to store the data (everything under the storage directory). This has served well, but has a few limitations, including no real support for native JavaScript objects like Date, Map, Set, and others. It also is unable to store data that contains "loops" — objects that reference themselves in some way. I'm not sure exactly when, but in the not-too-distant future I will publish a build using the new data format. It will automatically convert existing JSON data to the new format. For the moment, it will save data in both the new format and the old JSON format, preferring the former when loading data from storage. I have been running my own home with this new format for several months, and have no issues with data loss or corruption. A few other things to know: If you are not already backing up your storage directory, you should be. At a minimum, back this directory up every time you make big changes to your Rules, Reactions, etc. Your existing JSON-format backups will continue to be readable for the long-term (years). The code that loads data from these files looks for the new file format first (which will have a .dval suffix), and if not found, will happily read (and convert) a same-basenamed .json file (i.e. it looks for ruleid.dval first, and if it doesn't find it, it tries to load ruleid.json). I'll publish detailed instructions for restoring from old backups when the build is posted (it's easy). The new .dval files are not directly human-readable or editable as easily as the old .json files. A new utility will be provided in the tools directory to convert .dval data to .json format, which you can then read or edit if you find that necessary. However, that may not work for all future data, as my intent is to make more native JavaScript objects directly storable, and many of those objects cannot be stored in JSON. You may need to modify your backup tools/scripts to pick up the new files: if you explicitly name .json files (rather than just specifying the entire storage directory) in your backup configuration, you will need to add .dval files to get a complete, accurate backup. I don't think this will be an issue for any of you; I imagine that you're all just backing up the entire contents of storage regardless of format/name, that is the safest (and IMO most correct) way to go (if that's not what you're doing, consider changing your approach). The current code stores the data in both the .dval form and the .json form to hedge against any real-world problems I don't encounter in my own use. Some future build will drop this redundancy (i.e. save only to .dval form). However, the read code for the .json form will remain in any case. This applies only to persistent storage that Reactor creates and controls under the storage tree. All other JSON data files (e.g. device data for Controllers) are unaffected by this change and will remain in that form. YAML files are also unaffected by this change. This thread is open for any questions or concerns.
25 Posts 5 Posters 6.7k Views 5 Watching
  • wmarcolinW Offline
    I have a Tripp-Lite UPS (https://www.tripplite.com/smartpro-lcd-120v-1500va-900w-line-interactive-ups-avr-tower-lcd-usb-10-outlets~smart1500lcdt) that connected by a USB cable to my computer, reports various power supply and failure information, as shown in the panel below.
    The application I installed runs Java and opens the console to send the information.
    Has anyone tried to bring the information into the MSR? Or even a VeraPlus?
    • toggledbitsT Online
      toggledbitsT Online
      An integration requires something to talk to, and in my experience, most of these desktop applications for home/SOHO UPS systems don't offer anything. So first question is to find out if the application publishes a web service or has other similar capabilities.
      Failing that, you can use a NUT (Network UPS Tools) server, which can be configured for client access so that other systems in your network that are NUT-compatible can get UPS status info. But, you probably will not be able to run NUT and the Tripp-Lite app side-by-side, as they will both want authoritative control of the serial (USB) port. So going down this path, you'll have to use NUT as your control software for the UPS on your Windows system.
      I use NUT on Linux (and I have a Reactor controller for it that I can publish). I know nothing about it on Windows.
      K wmarcolinW 2 Replies Last reply
        K Offline
        K Offline
        kfxo
        @toggledbits said in Integrate UPS with MSR:
        I would be interested in trying out the NUT controller if you publish.
          As always Patrick, thank you for your attention.
          I will follow your recommendation at the weekend and see if I can then have control by NUT, if this is possible then I communicate to you with your usual kindness to help us to then have access via MSR.
          Thank you very much and I will inform you next week.
            toggledbitsT Online
            OK. I had to cobble-up some documentation, and I'm a bit swamped this week so forgive any spelling and grammar transgressions arising from my haste.
            NUTController build 22151 can now be downloaded from extras and the docs are here.
            K 1 Reply Last reply
              K Offline
              K Offline
              kfxo
              wrote on last edited by kfxo
              Getting this error in the log when restarting Reactor after performing the installation steps for NUT controller. I am on Reactor 22149 installed on Ubuntu in Docker.
              [latest-22149]2022-06-01T16:54:36.344Z <Structure:INFO> Structure#1 loading controller interface nut (NUTController)
              [latest-22149]2022-06-01T16:54:36.345Z <Controller:CRIT> Controller: failed to load nut implementation /var/reactor/ext/NUTController/NUTController.js: [TypeError]TypeError: Incompatible base version; is 22125, requires at least 22145
              [latest-22149]2022-06-01T16:54:36.346Z <Controller:CRIT> TypeError: Incompatible base version; is 22125, requires at least 22145
                  at Function.requires (/opt/reactor/server/lib/Controller.js:327:19)
                  at Object.<anonymous> (/var/reactor/ext/NUTController/NUTController.js:9:53)
                  at Module._compile (node:internal/modules/cjs/loader:1103:14)
                  at Object.Module._extensions..js (node:internal/modules/cjs/loader:1157:10)
                  at ModuleWrap.<anonymous> (node:internal/modules/esm/translators:168:29)
                  at ModuleJob.run (node:internal/modules/esm/module_job:197:25)
                  at async Promise.all (index 0)
                  at async ESMLoader.import (node:internal/modules/esm/loader:337:24)
              [latest-22149]2022-06-01T16:54:36.346Z <Structure:ERR> Structure#1 controller nut (NUT) skipped, implementation could not be loaded.
              edit: Fixed in build 22152. See below.
                toggledbitsT Online
                Whoops! Sorry. I'm using a slightly newer version of some classes. Fixed now, 22152 build of NUTController available for download.
                K S 2 Replies Last reply
                  K Offline
                  K Offline
                  kfxo
                  Confirmed fixed. Thanks.
                    NUT installed and running, it was a long way, I had to install VirtualBox and create a Linux VM because I couldn't find anywhere how to have NUT for Windows.
                    Now I see that to install NUTController you have to be Linux too? If your answer is yes, then I will have another huge journey, move the MSR from Windows bare-metal to this VM I created, and we will have to read a lot of manual, I know nothing of Linux.
                      toggledbitsT Online
                      It should run fine under Windows. Just create an ext directory in your Reactor install directory, unzip the archive, and copy the NutController folder into ext. If you look at the install.sh script, all it does is install dependencies using npm, so instead of running the script, just run the npm command manually:
                      npm i --no-save --omit dev
                      Configuration steps are the same, but depending on how your VM is configured, you may need to do some network tricks in VirtualBox to make sure that NUTController can access the IP port of your NUT server in the VM. Can't help you there. VirtualBox is not my jam.
                      wmarcolinW 1 Reply Last reply
                        22152 build of NUTController available for download.<
                        Thanks for publishing this. I am now using it on MSR Synology docker. Love it.
                          Hi Patrick
                          Well, I got all the installations done, and NUT is connected to the MSR.
                          Looking at the Reactor log, no error:
                          [latest-22149]2022-06-07T04:07:18.147Z <Structure:INFO> Structure#1 loading controller interface nut (NUTController)
                          [latest-22149]2022-06-07T04:07:18.158Z <default:null> Module NUTController v22152
                          [latest-22149]2022-06-07T04:07:18.272Z <Structure:INFO> Starting controller NUTController#nut
                          [latest-22149]2022-06-07T04:07:18.276Z <NUTController:NOTICE> NUTController#nut connecting to NUT server at "192.168.33.25":3493
                          [latest-22149]2022-06-07T04:07:18.278Z <NUTController:INFO> NUTController#nut started NUT client connection; waiting for ready
                          [latest-22149]2022-06-07T04:07:19.258Z <NUTController:INFO> NUTController#nut connected and ready!
                          [latest-22149]2022-06-07T04:07:19.260Z <NUTController:NOTICE> Controller NUTController#nut is now online.
                          In the VM using the command: upsc smart1500lcd@192.168.33.25 shows all the UPS data.
                          So, my difficulty as can be seen on the first screen, that I don't get the detailed UPS information in the MSR.
                            toggledbitsT Online
                            You are not searching correctly in the Entities list. Your UPS name does not have "nut" in it. Rather than seaching for entities containing the word "nut", clear all fields and select your NUTController instance in the controller filter field.
                              Perfect, and thanks again!!!
                                Hi!
                                A query, my NUT service stops working recurrently, and when I make the query upsc myups@localhost I get the message Error: Data stale.
                                To get it working again I have to run upsdrvctl start to restart.
                                Has anyone experienced this difficulty?
                                  Okay, job done, UPS > NUT > MSR > HE 😁
                                  The only thing that bothers me is that the UPS drive stops working without explanation, and I had to put a routine in crontab for it to restart every 10 minutes, I find this horrible but it was the only solution from everything I read, and I am not the only one to do it.
                                    toggledbitsT Online
                                    Does the NUTController's system entity show that the connection is down when that happens? If so, and NUT is running on the same host as MSR, it's probably pretty easy to just write a rule that restarts the NUT service when the controller has been marked down for X minutes (sustained for).
                                      The NUT and MSR are in the same HW, but NUT is in a Linux VM, and MSR I run in Windows.
                                      I was able to build a rule in MSR that analyzes 3 attributes of NUT, that if they stay without changing the content in 5 minutes gives me an alert of failure.
                                      Strange, when I look at the service, it is all active, what crashes is the UPS driver, so I have to run
                                      upsdrvctl stop
                                      upsdrvctl start
                                      Now, is it possible via Windows MSR to trigger a command in the Linux VM to do this restart? It would avoid having to crontab, only reboot in real failure conditions, and not every 10 minutes.
                                        Andr
                                        I rescued an Eaton Ellipse ups from work that come back to life with fresh batteries.👍
                                        Thought it would be easy to get some kind of system status or notification (from Windows) that somehow could be picked up in Reactor or at least in HA. Oh my... what a horror 😱
                                        After a long time following this guide I got NUT up and running on Windows @wmarcolin (Another VM is not a resonable option here)
                                        Monitor a UPS attached to a Windows machine
                                        Then I added the HA integration just to se if it worked and it actually did 😂
                                        So now I want over the finish line, and install NUTController in Reactor.
                                        It looked easy, but still, no luck.
                                        This got me thinking on another possible solution. Reactor already monitors "System Memory" "Uptime" and so on, so maybe it also could monitor Powersource, Battery Level, Charging State? Then let Reactor react with its magic @toggledbits ?
                                        For a Windows user that seems a lot easier and efficient as Windows just handle my UPS as the battery it actually is so it looked like "a laptop".
                                        Anyway, here is were I got stuck. No clue what more to try since the Nutserver is up and running and speaks with HA.
                                        reactor.log gives me two errors:
                                        [latest-23196]2023-07-28T19:34:28.862Z <Structure:CRIT> TypeError: self.nut.setUsername is not a function [-]
                                            at NUTController.start_client (c:\reactor\ext\NUTController\NUTController.js:221:22)
                                            at NUTController.start (c:\reactor\ext\NUTController\NUTController.js:44:14)
                                            at Structure.start (c:\reactor\server\lib\Structure.js:362:56)
                                        [latest-23196]2023-07-28T19:34:28.863Z <NUTController:CRIT> TypeError: Cannot read properties of undefined (reading 'end') [-]
                                            at Nut.close (c:\reactor\ext\NUTController\node_modules\node-nut\node-nut.js:65:15)
                                            at NUTController.stop (c:\reactor\ext\NUTController\NUTController.js:53:26)
                                            at c:\reactor\server\lib\Structure.js:366:48
                                        [latest-23196]2023-07-28T19:34:28.864Z <Controller:NOTICE> NUTController#nut stopping
                                        NUTController.js:221:22 looks like this
                                        Structure.js:362:56
                                        node-nut.js:65:15
                                        Structure.js:366:48
                                          toggledbitsT Online
                                          Go into the extension directory (ext/NutController) and run npm list and post the output here.
                                          Also you need to show your NutController config.
                                            100.5k
                                          • Next Release?