Sorry for a hasty post, will update some details later, but the scenario is that I managed to type a wrong password for too many times and had the following users.yaml section: authtrack: max_attempts: 4 within_minutes: 180 # 180 minutes = 3 hrs block_expiration_minutes: 10080 # 7 days At this time I used build 26298. Then noticed there's a new build with a bypass blocking feature (and yes, it said it won't remove existing block). Anyway, went ahead and upgraded to 26318, but the problem now is that UI is not loading at all (page does not answer). This also means that I cannot use "http://reactor_host:port/diag/clear_authtrack?askauth" command to clear the block (or use any other source IP for login). Docker container stays up & running and does not exit. I'll try to dig up some logs, but anything that I could immediately try out (could I delete a particular file for example)? EDIT: some logs [latest-26318]2026-11-17T20:42:32.337Z <Rule:INFO> MSR startup (rule-lculfnhm in Miscellaneous) started [latest-26318]2026-11-17T20:42:32.343Z <httpapi:NOTICE> httpapi#1 HTTP server listening on :::8111 [latest-26318]2026-11-17T20:42:32.347Z <httpapi:INFO> httpapi#1 local docs found in /opt/reactor/docs/html; setting up static service [latest-26318]2026-11-17T20:42:32.354Z <app:NOTICE> Starting WSAPI... [latest-26318]2026-11-17T20:42:32.355Z <wsapi:NOTICE> wsapi: starting version 26298 protocol [latest-26318]2026-11-17T20:42:32.523Z <Engine:INFO> Engine#1 master timer tick, local time "17/11/2026 22:42:32" (TZ offset 120 mins from UTC) [latest-26318]2026-11-17T20:42:32.542Z <Engine:NOTICE> Starting reaction MSR startup<SET> (rule-lculfnhm:S) [latest-26318]2026-11-17T20:42:32.545Z <Notifier:null> Module Notifier v26186 [latest-26318]2026-11-17T20:42:32.545Z <Engine:INFO> MSR startup<SET> all actions completed. [latest-26318]2026-11-17T20:42:32.557Z <Rule:INFO> Rule#rule-lculfnhm reaction rule-lculfnhm:S completed [latest-26318]2026-11-17T20:42:32.558Z <default:null> Module NotifyTelegram v26177
    @therealdb I noticed a similar behaviour with build 25208, although the issue might have been present also in the earlier (25201) build.
    In essence I have a rule with a global variable correctly triggering when it has a certain value, but in reactions it has a Telegram notification using a local variable as message (like this: ${{ msg }}). And this local variable "msg" is using the same global variable that triggered the rule, but its value is something totally different, i.e. seems that it's not updating.
    I'm also sure this rule was working fine before, with variables correctly updating.
    @tunnus said in [Reactor] Variables not updating correctly in latest-25201-2aa18550:
    You know what to do (i.e. what I need to see). I can't do anything from just a post like this.
    My simple test case:
    1. I have a global expression/variable testVar (expressionless) with a numeric value assigned.
    2. I have a rule that triggers on testVar changing, and sends me a notification in its SET Reaction (shown below).
    3. I have a Reaction that I can run manually to increment testVar by 1 using a Set Variable action. This triggers the rule.
    This works as expected: when the Reaction is run, testVar is incremented by 1. The change is detected by the rule, which updates its localtest variable and then uses that in a notification, which displays the correct value.
    To be clear here, the Rule triggers on the global variable changing, not the local variable.
    tunnusT 2 Replies Last reply
      @toggledbits I did a very similar testing arrangement and got the same results as you, i.e. working fine. I guess I have to monitor this more closely and if this update problem happens again, find a way to reproduce it consistently.
      One notable difference between my production expression and the test expression is that the production one is a lot more complicated:
        @toggledbits, some extra information that I hope will help solve this. I've noticed a few other instances where variables aren't updating. These happen to be Telegram notifications, although I don't think Telegram itself is the issue—it's just that I tend to notice notifications more easily than changes in the UI.
        In all cases, a common denominator is that local variables (in my case, 'msg') that include other local or global variables also contain "if/else" and/or "case" statements.
        Examples below:
        msg =
        solar_last_day == "ERROR" ? "Error retrieving solar stats" : (solar_last_day > 1 ? "Daily solar stats are ready, total " + round(solar_last_day, 1) + " kWh, peak " + peak_array[0] + " W" + " @" + peak_array[1] : "NA")
        msg =
        case
          when success == true: "Export limit activated, sell price " + round(g_NordpoolCurrentPriceSellReal, 2) + " c/kWh (VAT 0%-mgin), grid balance " + round(g_FronPowerSum, 0) + " W"
          when success == false: "Export limit could not be activated?"
          else "Setting export limit failed"
        I'm not sure if it's related, but there was a recent bug involving global expressions not updating when certain functions were used (fixed in build 25082)
          I'd need a full picture of this... every variable and rule involved. This is a very complex area to look at.
          Again, the key rule to understand here, is that the local variables in a Rule do not update every time a global or other local they refer to changes -- they only update when the Rule has been marked for evaluation. The recomputation of the local variable values occurs before trigger conditions are evaluated, and only then. That is very different from the way global variables are handled.
          Also in your second example, the use of "==" is a "loose" comparison. The use of "===" is tighter and matches type. In your example, if success is 0 (numeric), that will satisfy the test success == false -- that's true because numeric 0 will cast to boolean false, so they are logically equal, although not exactly equal. That alone would explain unexpected results, if the values of success can be other than true or false.
            @toggledbits "success" variable cannot be other than true or false, that I know.
            But is it so that every time a rule is triggered, its local variables are evaluated (or should be evaluated) at least once?
            Also, you wrote earlier: "If there's already a pending request for re-evaluation queued, new requests are ignored. This is all to prevent infinite loops in rule evaluations where rules manipulate devices and rule-based variables in Reactions that are also part of the rule's dependencies"
            I was wondering if this could happen in cases where re-evaluation is queued but somehow gets stuck, and because new requests are ignored, updates won't occur?
              Well, they won't get stuck, but there is no guaranteed order to the re-evaluation. Other things waiting to execute can run before the re-evaluation happens, including things that could change the global variables or entity attributes on which the first Rule depends.
              Here's something to try (it's the @therealdb solution he mentioned):
              1. Make msg an expressionless local variable.
              2. Before your notification, use a Set Variable or Script Action to compute the value of msg that you want to send in the notification.
              Would look something like this:
              ...or this, using a Script Action...
              I personally prefer the Script Action because you can set several variables at once in the script, if that's what you need, and the syntax looks cleaner (you don't have to use the ${{ }} substitution.
                Yep, I confirm I had to update a couple of rules where I had similar variables as @tunnus
                I used script action because it’s multi line and definitely better in terms of readability.
                  @toggledbits ok, I'll have to try script action. Still, as @therealdb stated, I'm also sure the "old style" used to work with pre-252xx builds.
                    Some strange results happened while I was experimenting with script action. I noticed that the order of local variables had an effect whether those variables did update or not.
                    If I had e.g. the following order:
                    "peak_power" did not update. But if I switched places of "ok_to_reset" and "peak_power", "peak_power" started to update in real-time:
                      Post your script. Based on the instructions given, your local variables should be expressionless, so that seems wrong and I want to see what your script is trying to do.
                      I can tell you right now, if ok_to_reset is expressionless and you are resetting it in the Script Action script, and expecting peak_power to see the updated value, it won't work.
                        @toggledbits that wasn’t what I was trying to convey here. Let’s forget script action for a moment as it has no relevance for my finding.
                        What I’m trying to say here is that by merely changing the order of variables (and to be clear, that setup has worked before), my rules are working again. Somehow new builds do not like if expressionless variables are in the middle of regular ones. If they are last in line, all is well. Sounds crazy, but please test.
                          I'll say again, local variables are not processed/evaluated in the same way as global variables. Local variables are only evaluated when the Rule to which they belong is being evaluated (i.e. its triggers are being checked). They are not evaluated when a dependent local variable is changed. When the Rule is evaluated, its local variables, if any, are evaluated before the triggers, and yes, they are evaluated in the order in which they are defined. That is known.
                          Combine this with using a Set Variable action... if you don't check the "Force re-evaluation" checkbox, any other local variables that use the variable being set will not be updated until the Rule is next evaluated. If you check the box, it forces a Rule evaluation, and it is the second evaluation that will update the dependent variables.
                          The Script Action is absolutely relevant in your case, at least from what you've posted, because you apparently still had local variables that are dependent on the local variable that the script was changing, and that was not consistent with my recommendation. The script will not cause the dependent variables to be updated, because there is no "Force re-evaluation" option for the script, and local variables are not dependency-scanned/triggered, as I said above. That means your script action will change the local variable ok_to_reset, but that won't make peak_power change immediately after. That is why I recommended that you make all local variables expressionless when using the Script Action, and do all of the work in the script, none of the work in the local variables' expressions.
                          None of this is new. And again, no changes have been made to how variables (global or local) in any of these recent builds. The earlier changes you mentioned to make isRuleSet() and isRuleEnabled() trigger with the rules they reference (build 25082 -- a long time ago) was a change to the implementation of those functions themselves , but was not in any way a change to the mechanism that handles changes in global expressions.
                            @toggledbits I’m not using script action currently, and those screenshots were from a rule that uses set variable action.
                            But could you test my finding? Even rule triggers are not relevant when reproducing this finding. Just put a variable referencing an entity which frequently changes as a first one. Then make expressionless variable second, and as a third one make some kind of expression which uses first variable and does some calculation with it. Observe what happens and then swap second and third line and again watch what happens.
                              @toggledbits have you had time to look at this? I suspect there’s a bug in evaluating local variables when expressionless variables are not last items in the list
                                It works as I would predict.
                                  @therealdb could you test this if you could get your original rules (variables) to work just by rearranging local expressions? My hypothesis being that expressionless variables should be last in the list
                                    @therealdb & @toggledbits, below you can find my simple test case for this case. At least in my setup I can consistently reproduce this behaviour. (Still) using build 25208.
                                    1. First, make sure you have some device/entity which updates often (not strictly necessary, but it's faster to see the results & differences).
                                    2. Then put "target" variable immediately after "source", and "expressionlessVariable" should be the last one
                                    3. Now "target" should follow/change as "source" changes
                                    4. Next, swap "target" & "expressionlessVariable" (as seen in the image). Save.
                                    5. Now "target" ceases to update
                                      #24
                                      It's probably moot at this point... I've just spent the last two weeks completely revamping the evaluation of Rule-based variables, to make them perform more like global variables, respect dependencies between them better, etc. The last week has just been a deep dive through the logs watching the performance of my own house on the updated approach.
                                      I'll shortly be releasing a blind build with these changes, just for you (@tunnus) and @therealdb to try. I expect this to be disruptive, because any approaches in the logic that rely on specific behaviors and side-effects of the old approach will now work differently, maybe fail, and adapting to the new approach will be necessary. But, I think the new approach will produce a result that is much more in keeping with how you would expect it to work. So, sit tight... I'll be ready to build later today or early tomorrow.
                                        #25
                                        OK. Interim build latest-25248 for 64-bit docker systems only is up for testing/trials.
                                        NOTE TO ALL USERS NOT CONTRIBUTING TO THIS THREAD — this is not an official build and you are advised not to upgrade to it just yet. This build is specifically for participants in this thread as we work to improve the behavior of Rule-based variables. Wait for a build advertised in the official announcement thread before upgrading your system.
                                        Behavior of Rule-based variables now:
                                        • Will still be re-evaluated when the Rule is started, and any time the Rule is subject to trigger condition check (i.e. behavior not changed);
                                        • When the trigger condition check occurs, Rule-based variables are always evaluated/updated before trigger conditions (i.e. also same as before);
                                        • Rule-based variables may be modified by Set Variable action and assignment statements in Script Actions in Rule Reactions (unreliable before);
                                        • If a Rule-based variable references another Rule-based variable, and the latter changes, the former will be re-evaluated (now same as Global Variables).
                                        • The order of Rule-based variables doesn't matter, it's just for your convenience. Dependencies between variables are established at startup, and evaluation takes place in dependency tree order, not the order shown in the UI (now same as Global Variables).
                                        If you run into an issue you can't resolve, here's what I ask:
                                        1. Make sure your expectations are aligned with the changes above; make sure you are not relying on any prior behavior or side-effect of the prior behavior.
                                        2. Enable logging for the rule in question. Put a snippet like below in your logging.yaml file (replace the part after # with your rule ID):
                                           "Rule#rule-l3hj06aa":
                                             level: 5
                                             streams:
                                             - type: file  # filename is derived from rule ID
                                               keep: 2
                                               level: 999
                                               recycle: true
                                        3. Restart Reactor and get the rule in question to demonstrate whatever the issue is. Make sure to then capture the log file called Logger#Rule#XXX.log... I will be asking for it.
                                        4. Report the issue here on this thread, with all of the usual attention to posting requirements: good, detailed description; expectations of behavior; clear description of what's not meeting expectations; etc.
                                        5. I will PM you a URL where you can upload the log file and your rule JSON file (from storage/rules) if necessary.
                                        The locally-installed version of the documentation is also updated.
                                               level: 5
                                               streams:
                                                 keep: 2
                                                 level: 999
                                                 recycle: true
                                          @toggledbits whoops... guess this is one time having the system auto-update containers with new images is bad....
                                          So I'm on the test version. Found this:
                                          This is a Dynamic Group I'd created forever ago:
                                          My ruleset:
                                          23a5760e-ff12-45c2-b30e-11a08a13138b-image.png bc3bb93c-572b-4d5c-a718-fcbde56d7abb-image.png
                                          I added the snippet as noted into my logging.yaml file:
                                          When it didn't work I checked my yaml and found a spacing issue. That's been corrected, I now have a proper logger* log. Will upload to our pre-x Dropbox in folder 25248 logs along with the rule JSON file.
                                            163.9k